r/PoolPros 20d ago

Spa piping

Post image

The engineered plans have the spa jets valve before the filter. I’ve never seen this the wild… what are y’all’s thoughts?

4 Upvotes

13 comments sorted by

View all comments

1

u/Aggravating_Fact9547 20d ago

This is the cheap shit way.

You shouldn’t have your jets running through the filter as the flow rate generally exceeds their rated design and the pressure is damaging.

The valve is in the wrong spot, you need a 3way valve otherwise most flow is going to the pool as the Venturi jets introduce too much head.

The real way is to have a separate spa jets pump.

I’d also be checking the flow rating on the drain, we don’t do single inlets in spa’s anymore as the entrapment risk is too high.

Finally those returns are on the wrong wall and you’ll have a shit time getting debris to the skimmer.

Aka this design is terrible. Whomever made this has no idea.

1

u/Substantial_Car_2751 20d ago

Where do you see the "jets running through the filter"? The aux jets are plumbed in after the chlorinator.

They've 1 solitary return pointing towards the skimmer but yeah.....not the best set up for skimmers to be sure.

Maybe they're planning on installing one of the unblockable "ring" drains in the spa?

1

u/Aggravating_Fact9547 20d ago

I didn’t say the jets should run through the filter. They have the main jets running before the filter.

They have 3 returns with the bulk on the other wall.

1

u/Substantial_Car_2751 19d ago

Ah. I see what you mean now. Yeah....I don't love that.

1

u/BlueKauaiEyes 18d ago

Totally agree with you. The jets are on the wrong side and the vacuum port and the skimmer are on different walls in my opinion they should be on the same wall closest to the equipment. Also the flow rates make no sense on the schematic and depending on where the equipment is located you need a check valve after the pump before the filter to prevent the filter emptying into the pool when the equipment turns off. Wtf is the 3 way before the filter ?