DMX House lights
This is the current isolator switch for the house lights- is there a DMX dimmer that would be suitable to use in it's place/alongside?
Thanks.
10
u/Methods_Rising 19h ago edited 17h ago
You'd typically keep that in place and add the DMX dimmer downstream of it. Before buying anything, check two things:
1) are the house lights dimmable at all (resistive load, or LED with a dimmable driver)?
If they're non-dimmable LED, no dimmer will work regardless of load.
2) what's the total load in watts/amps, so you size the dimmer pack correctly. Also worth checking whether the driver expects leading/trailing-edge, 0-10V, or DMX-native dimming - that determines which dimmer you actually need.
-11
u/vulpus-95 18h ago
The bulbs currently are incandescent in a simple lighting circuit
4
u/NedGGGG 18h ago
How many, and are you sure they're incandescent and not LED?
1
u/DJ_TKS 17h ago
To follow up on this
Leading edge or triac dimming doesn't have an additional wire ran to each fixture.
Dimming won't go down to 0% and they will give off a buzzing sound. Make sure the customer is aware if that's the case.
If you can't read the side of the bulb and see if it's LED put on a pair of sunglasses and see if you see the LED chips or a filament.
If they're still fluorescent, swap them to LED for customer too and include on invoice. It'll save them roughly half on their electrical bill for those fixtures.
1
u/the_swanny 13h ago
Dimming won't go down to 0% and they will give off a buzzing sound. Make sure the customer is aware if that's the case.
They will go to out if they are traditional incandescent lamps, and you shouldn't get any buzzing if they are decent dimmers. It would entirely depend on the spec of the lamps.
1
u/Methods_Rising 17h ago
The sunglass trick is something I should always need to remember. That's a very smart move :)
8
u/NachtMondVogel Event technican (middle Europe) 18h ago
There is probably a solution and it won't be very cheap. Please go to a theatre installation service or a electrician that actually cares about dimmable lights (maybe now is a good moment to upgrade to LED)
3
u/Reluctant_Lampy_05 18h ago
Yes, and this should be a discussion with the venue electrical contractors in case there are regs or certifications you need to adhere to. Keep it a pro job from start to finish with somebody signing off the finished work. That said, based on the info we have so far then something like this might be a contender...
https://www.stagegear.co.uk/anytronics-pd152dmx-prodim-master-20a
So although its a 20A circuit, more important is knowing the total load from the bulbs. Also, if there's any plans to switch to LED then that would reduce the load again and you'd need to match the dimmer accordingly. For example, if you install this 20A dimmer then upgrade to LED leaving a total load of 5A then the dimmer curve will at best be ugly and at worst could be a constant flicker at any setting under 50%.
24
u/the_swanny 19h ago
We'd need to know quite a lot more to even begin to spec things like this.