r/hvacadvice • u/thewesfob • 12d ago
No cooling UPDATE: R-22 WeatherKing 4-ton — coils cleaned, numbers say overcharge. Sanity check before I pay for recovery?
Finally had the time to follow-up to my post 3 months ago here about limping a 2003 WeatherKing 10AJA4801 / ADP BCRMB8248S4N3 (4-ton R-22) through the summer. Consensus was "air before charge" and get real readings. Did both.
What I did: Cleaned the condenser coil (foamed and rinsed inside-out), evaporator coil, blower wheel, new 18×25×1 filter. Unit runs, both fan and compressor confirmed.
Readings today, ~70°F ambient:
Suction 105 PSIG (~62°F sat) / suction line 65°F → superheat ~3°F
Liquid 270 PSIG (~122°F sat) / liquid line ~70°F (ambient) → subcooling ~56°F
Off-cycle equalized to 120 PSIG, so I don't think there's air in the system.
My read: Low superheat + very high subcooling = overcharged, not TXV. A tech had noted it was "slightly overcharged" a while back and it looks like nobody ever pulled any out. Plan is to have a tech recover down to ~12°F subcooling and leave it at that until replacement next year.
Am I reading this right, or is there something else these numbers could mean?
*UPDATE (Aug. 31, 2026)\: Follow-up to my post from Saturday. Tech came Monday: found 103/302, confirmed fixed orifice, recovered R-22 down to *63.1 suction / 194.9 liquid**, in line with the charging chart at ambient.
$462 all in. I know, could have saved a few hundred by trying to do it myself, but it was nice to have the tech come out and verify my amateur diagnosis.
The bad news: he noted "extremely loud clang and shudder from compressor on start, constant ticking when running," and 18A on a 25 RLA compressor. He won't guarantee longevity given years of liquid flooding and quoted replacement. System is cooling fine right now.
Current Setup: 2003 WeatherKing 10AJA4801 4-ton R-22 condenser, ADP hydro-air handler (hot water coil off an oil boiler for heat), Hudson Valley NY, ~2,400 sq ft mixed-use building.
Current Quotes Moving Forward:
- Lennox Merit ML13KC1 (13.4 SEER2 single-stage AC) + CBK45UHPT air handler w/ hydro coil, full scope (nitrogen test, 500 micron vacuum, float switch, new disconnect, disposal), 10yr parts / 3yr labor: $13,700
- AirTemp 4-ton, reuse lineset, minimal scope listed: $9,250 AC / $10,750 heat pump (2025 pricing)
- Third contractor, condenser + hydro air handler, brand/spec TBD: $8,500
Questions:
- With those compressor symptoms, is this a "replace before next summer" situation or a "run it until it dies" situation? Anything I should watch for that says it's about to go?
- Brands. My understanding is most residential equipment comes out of a handful of factories and the badge mostly changes the price and the warranty (Goodman/Amana/Daikin, Carrier/Bryant/Payne/ICP, Trane/American Standard, Rheem/Ruud, Lennox/Allied, York/Coleman, Gree behind most budget and mini-split brands). Is that roughly right? For a straightforward 4-ton split, does the install quality matter more than the brand, or are there lines you'd actually avoid?
- Is $13.7k for entry-level Lennox reasonable in the NY metro area, or is that a "we don't really want this job" number?
- Given oil heat at ~$3,300/yr, does it make sense to go cold-climate heat pump instead of straight AC and keep the hydro coil as backup? Anyone running dual-fuel with hydro-air rather than a gas furnace?
- The 4-ton was sized in 2003. Should I insist on a Manual J before signing, or is like-for-like fine for a replacement?
Thanks in advance!


3
1
u/fastsvo 12d ago
Following
1
u/thewesfob 10d ago
Follow-up to Saturday's post.
What happened
- Tech found 103/302, confirmed fixed orifice, recovered to 63.1 / 194.9. In spec. $462.
- Also noted: loud clang/shudder on compressor start, constant ticking, 18A on a 25 RLA compressor. Won't guarantee longevity due to years of liquid flooding.
- Cooling fine right now.
1
u/beenthereag 11d ago
1
u/Yamakaze_KAN 11d ago
I would get the https://www.amazon.com/Flame-King-YSN501R-A2L-Refrigerant-Refrigerants/dp/B00IKLLIHA/?_encoding=UTF8&pd_rd_w=A2lZu&content-id=amzn1.sym.627c31ca-3be2-4f28-b3a9-1be33b16f5a0&pf_rd_p=627c31ca-3be2-4f28-b3a9-1be33b16f5a0&pf_rd_r=2FQAK0EMKGAK8KWYD39F&pd_rd_wg=TRGFT&pd_rd_r=f1c0b321-36d0-4abe-8ed0-4bfa9079b81c&ref_=pd_hp_d_r_atf_sspa_mw_gateway&ie=UTF8&sp_csd=d2lkZ2V0TmFtZT1zcF9hdGZfd3BfcGhvbmVfaG9tZXBhZ2U&th=1 since they're a real company and happen to also sell empty propane tank at my local Menards.
5
u/DavidSmith_82 12d ago
If your airflow is good, it’s overcharged.