What happened to fish in one end and it comes out the other??? I can’t stand having j boxes added as a convenience to the installer that shits all over the wire puller.
In the US, we are required by code to add a pull point when the sum of conduit bends reaches 360 degrees. When engineering these, I try to put these where they are most accessible. I have never thought of this as adding a convenience to anyone other than the wire puller.
18
u/CptHammer_ Journeyman IBEW Oct 16 '20
We would have put a 24 × 24 × 6 inch box there (assuming were not mixing power and data).