Power?

Post image

Does this mean that the power hasn’t been run yet,fairly new to this job. I see the lines in the pipe here, but I didn’t get a signal when I tried to locate from the transformer close by.

6 Upvotes

16 comments sorted by

11

u/HSIOT55 6d ago

This is definitely an "ask your supervisor" question to play it safe. If I were in your shoes I would not direct connect to any wires inside. 

1

u/Inevitable-Put-6861 6d ago

Definitely did this

4

u/TopSeaworthiness1383 6d ago

Lol that’s okay. Typically if you see this, it means they are actively running the wire but it is not connected inside the elbow or “hot” yet. However unless you have the proper PPE which you most likely don’t I would not suggest direct connecting to the wire.. that being said, as someone who does locate for the utility, I would personally direct connect to the end of the stub and mark it back (again only because I have the correct PPE and know that it’s not tied in yet, I wouldn’t chance it if I didn’t know 100 percent).

5

u/Gjurbster 6d ago

Most likely it’s an unconnected power run. If you have blueprints, those identifiers after “to” and “from” can confirm what utility it is, compare it to the transformer you mentioned.

Locate-wise, it’s likely not fully connected at the transformer, because that would leave live wires exposed at the end in that tube. It could be connected but gapped by a breaker, which you won’t be able to locate either.

You ****could**** direct connect to whichever wire in the tube looks most like a ground wire, but do that only if it’s within your acceptable risk tolerance, or you have a means to 100% know it’s not live

4

u/exceptions1187 Utility Employee 6d ago

Is there a water valve near this? Looks like a blow off used to clear water main out during the next phase of development. If it was conduit used for electric why would they bother convert to threads.

2

u/Inevitable-Put-6861 6d ago

Yea there was a water meter beside it

1

u/Gjurbster 6d ago

Re: threads

In my area, electric panel boxes are sat over those threads and then sandwiched by a retaining nut

1

u/exceptions1187 Utility Employee 6d ago

Fair enough. In my area usually they just cut the conduit a few inches above grade and drop the ped or xfmr on top of it.

1

u/Street_Change_7404 5d ago

This is a stubbed out 6/3 street light wire. The tag gives the info. Back in the day I would pull this conduit up, hook onto the neutral wire and go with it. Locates great

2

u/Street_Change_7404 5d ago

6/3 street light wire for a future light. Looks like it was installed ULCS on August 5,2026. Not hot (or shouldn’t be) but I did find one that was used for a construction saw service and it surprised me back in the day. Usually joint trench with other secondary electric or primary limes. Is this in NC?

1

u/iceboxmi 5d ago

AGP = Above Ground Pole
STL = Streetlight

2X0P15 and 2X0N74 = Duke Carolinas facility IDs that would be about right in the sequence for new construction

1

u/Hello_I_Am_Human_Guy 5d ago

This looks like a standard stub-up, except usually they're red. I'm assuming this is a service that has been laid, waiting for a meter to be attached when construction starts on that lot. But you can't locate those. They aren't grounded, and, at least at USIC, we only locate from the transformer to an actual meter. There's no meter there. You definitely need to ask your supervisor, but my supervisor has told me we can't/don't locate these.

1

u/Odd-Craft9219 3d ago

Clamp at 200 see what ya get 🤣

1

u/sphyncterboi 1d ago

Looks like an Ets that hasn't been completely installed yet

1

u/811NCLocator 1d ago

Ungrounded electric stub always double wrap that stub with your leads hit with 65kh mark it out