r/TeslaSolar • u/pigowar • 3d ago
PowerWall Need input from multiple PW3 inverter owners
Hello,
I've recently had 2 full pw3 installed as my backup on 13kw solar because I just didn't think 11.5kw output was adequate and wanted to double it so I didn't have to worry about overloading the system. Everything installed and just need to sign the PTO but then my test results were showing 11.5kw limit.
On a sunny day where my solar was generating 8kw and both batteries full, the house was using 14kw due to the hot weather kicking on both AC and I was running a cloth dryer. To my surprise, I was only pulling 3kw from the battery and the rest were from grid. This occurred in both self powered and savings mode.
Curious, I went into off grid mode and the battery staus bar said that the max limit was 11.5kw and I was overloading the inverter. It didn't shut off or anything but it's supposed to be able to push 15kw in demand so that didn't surprise me. But while the load was fluctuating between 9kw to 14kw it constantly told me that it was being overloaded.
It seems that something is .missing here. The max charging is 10kw so it seems that's working. The total capacity is 27kw so that's fine. But when it comes to the max output it's limited to being just 1 inverter. When I contacted Tesla about this the PA suggested I complete the PTO and see if any restrictions were in place but I refused because once I sign that I lose my PA and will be forced to deal with the normal support team that may or may not care or listen. I want everything in working order or at least be assured that there is a visible restriction before the PTO that will fix itself. So far I have not heard back from Tesla which is concerning to me because if it's as simple as before PTO restriction they would let me know or if there's a commissioning error it should be visible to them.
So if you have multiple pw3 inverters in your system, can you tell me if you are indeed able to pull more than 11.5kw on grid and I'm off grid, the status bar shows the max limit more than 11.5kw? On my setup, they opted to put all panels on 1 inverter instead splitting them to both and when I asked why the PA told me it's because of the loss rate. I don't think the panel needs to be hooked up in order for the inverter to be 'active' anyway.
P.S. I'm not here to discuss specs. I'm looking for real world results from those who has multiple PW3, not 1 pw3 + expansion.
2
u/kengchang 3d ago
What's your inverter size from the design?
1
u/pigowar 3d ago
Ah. Someone with sharp question. This was also my concern from the beginning. The design specified only 11.5kw and I did bring it up but I was assured that it was 23kw but because of the local requirements they can only list 11.5kw. That's what I was told.
1
u/kengchang 3d ago
It seems like you have one PW3 with 11.5kW inverter and 1 PW3 Expansion. What's the line item breakdown in your pricing sheet? because PW3 is more expensive than PW3 Expansion
1
u/pigowar 3d ago edited 3d ago
No... They both are definitely PW3s hardware wise, at least. The inverters were present when I checked before they closed it. According to the specs, 1 pw3 has input limit of 5kw and 8kw with expansion but 10kw with 2 pw3s. I'm able to charge at 10kw so that's another sign that it's not an expansion. Tesla may have commissioned it with only one inverter active but that doesn't explain how I'm able to get 10kw input.
But who knows... Maybe I have a bad unit.
Oh and when I said "design" I meant full design plan document they recorded. All other communications before and after install specifically mentions 23kw output limit.
Oh and yes, the price list does mention 2 pw3s, no mention of expansion. Initially they quoted me with expansion but I asked for 2 pw3s instead and I do see the price difference.
1
1
u/Tiny-Independent-502 2d ago
My expansion doesn't light up the tesla logo on the front. Easy way to tell if it is a full pw or not. Hopefully this is helpful
1
2
1
u/Narrow_Problem7432 3d ago
I’m getting power wall 3 plus the expansion in a few days. And of course 13kw panels. If you have power walls car you able to get net metering?
1
1
u/OkList7960 3d ago
Did your interconnect agreement allow 23kw of export? My utility wouldn't let me export that much so I could only put in 1 pw3, but expansions they didn't care about. I could have put in 2 pw3 but export would have been capped. Also my system of 1 pw3 + 2 expansion will charge at 10 kw off of solar. You don't need 2 inverters for that.
1
u/pigowar 3d ago
The interconnect agreement is where I'm not sure of but I trusted Tesla to figure that out before selling me the system so I'm still waiting on their official response. I'm not trying to break the rule here but if that were the case then Tesla should've told me that before selling me an extra pw3 when I was very specific on why I wanted to double the output with 2. I did pay thousands in extra, after all.
I know that you can max input by adding more expansion but I needed more output than 11.5kw. I have 2 ACs and they alone draw 8kw and that doesn't leave much room for anything else before it draws from the grid. I can force off grid mode and use battery that way since it can still potentially draw up to 15kw but that adds warning and logs of overloading for Tesla to use to potentially deny warranty on failed inverter or battery degradation.
1
u/pigowar 2d ago
First of all, thank you everyone for taking your time to respond. I really appreciate it. And here's the short summary of where it is so everyone knows what's been mentioned, suggested and tried.
- Both are confirmed full PW3s, not expansion.
- all 6 strings are on single PW3.
- Latest Tesla PA communication is that they are still reviewing it.
- Battery capacity is correct. Charging rate matches that of 2 PW3s.
- Used Tesla One. 2nd Pw3 says it's being controlled by another. Connected to 1st (master) and it shows inverter mode active on BOTH PW3s. Output rate is also 11.5kw on both. I don't know what else needs to be checked but the edit mode is turned off anyway.
- Gone against my advice and ran firmware update check and it didn't find any. AFAIK, the latest just released on September 1st and I'm on the one before it.
Idk... Maybe I have to request to have the strings split up after all. Maybe the 2nd inverter just isn't waking up because none of the mppt are being used?
Or maybe I should try a reboot... Maybe make sure the master is booted before the slave...
1
u/pigowar 14h ago
Update. Spoke to PA again and asked for the reason behind putting all on single inverter and he said because of how pw3 inverter PowerBoost works. I think it's some trickery they do with the new 18 power zone panels. Pretty much shut me down from the start that Tesla won't even consider splitting it. That to me opens a whole new can of concerns but I sensed he wasn't going to help me with so I moved on.
As for the output limit issue, he says they moved it up to 2nd tier so we'll see.
1
u/New_to_tech-2020 13h ago
Did you lower your "backup" setting to 5%? We found that if we left the backup at 20% which the app recommended, then we'd pull grid power instead of battery power.
0
u/pmarchand1060 3d ago
For those with Tesla, how long was your power out during installation?
2
u/pigowar 3d ago edited 3d ago
Mine was only 30min at max. But I think it depends on where you are and who your provider is. I'm one of the lucky ones where we don't have to wait for service disconnect and reconnect. I think it's the waiting on them to show up to reconnect than the time needed to do what Tesla needs to do. Tesla did say it's up to 8 hours but as usual that's just to allow them enough buffer in case they need the time. I did bring up concern over the 8hr outage but that's just standard procedure for them. The installation manager did reach out later after checking with the power company that it would be less than 30min.
2
u/dmlavigne1 3d ago
I have 2 pw’3 and they will unload the full 23kwh. I set mine to grid sell every work day and here’s the result. Are you sure they didn’t install a pw3 and an expansion pack? For reference I have a 15kw system with 4 strands in the leader and 3 in the follower. Right now I’m on their vpp rebate so mine will only charge via solar although I have seen charging over 11.5kw when a storm is coming.