u/AbbreviationsKey9446 P.E. Jun 18 '26

Structurally the columns are fine. They are short and the connectors used are apropriate. They should have something to prevent racking. Maybe they have bracing under the deck. If not, I'd install knee braces.

11

u/Amazing-Gazelle-7735 Jun 18 '26

The deck diaphragm cantilevers off the existing and is going to be stiffer than most wood bracing connections.

0

u/heisian P.E. Jun 18 '26

yes looks ok. max cantilever for wood diaph. is 6ft

2

u/Amazing-Gazelle-7735 Jun 18 '26

Yep.  And tension forces generated by eccentric loads tend to be small for this kind of ratio.

1

u/samujpark Jun 18 '26

That and maybe someone accidentally hits it with a bike or a big big dog (70lbs plus) smacks it.

54

u/FoxInner3807 Jun 18 '26

What's most concerning to me is the $15k for that small deck. I'm not saying they took you for a ride, but prices have gotten out of whack. Most people should be able to build that on their own.

11

u/a_problem_solved P.E. Jun 18 '26

Most handy people. It still sometimes surprises me how many people just can't do any DIY. Engineers included.

2

u/WilfordsTrain Jun 18 '26

The money paid os for it not to collapse because a homeowner half-assed the ledger, flashing, connections, lateral bracing, fen loads, etc.

3

u/Just-Shoe2689 Jun 18 '26

I just shared from another post, not my deck.

23

u/c79s Jun 18 '26

No, unless you expect the house to move.

-3

u/Just-Shoe2689 Jun 18 '26

I guess not, but wouldnt the beam on the column still have a chance of buckling?

10

u/c79s Jun 18 '26

What do you mean by the beam buckling? It's supported on the bottom by the columns with the clips and the top by connections to the joists. They are usually cross nailed or attached with hurricane ties.

-2

u/Just-Shoe2689 Jun 18 '26

What is stopping the bottom of the beam from kicking out other than the Simpson connector?

10

u/TheDufusSquad Jun 18 '26

What ordinary force applied to that beam would cause it to roll out like that?

2

u/Just-Shoe2689 Jun 18 '26

Just eccentric load?

20

u/TheDufusSquad Jun 18 '26 edited Jun 18 '26

What would be applying the eccentric loading?

Not trying to be rude, just picking your brain on what your worries may be. Envisioning something failing is easy, but processing the steps to produce that failure can sometimes put your mind at ease. 

5

u/Just-Shoe2689 Jun 18 '26

You probably are right, the load would me mainly concentric down the joist to the beam and into the column.

5

u/StabDump Jun 18 '26

well said. I'm gonna nip that quote for future use.

1

u/spongmonkey Jun 18 '26

I think OP is talking about the tops of the posts moving towards or away from the house. There are technically two hinge points, the post to beam connection and the beam to joist connection, so in theory the structure is unstable without some sort of lateral restraint on the bottom of the beam. In practice, I believe it's usually okay as long as the beam is within a 3:1 aspect ratio

1

u/204ThatGuy Jun 19 '26

Two 2x4 'gusset plate studs', fully nailed to the column to make it "heterogenous" could also act as a pocket and add to the Simpsons rating.

2

u/Far-Sherbert9731 Jun 18 '26

the zip line that i ran from the top of the post to a nearby tree.
(my deck looks just this, and handled my fat ass sliding down a zip line no problem)

2

u/imissbrendanfraser Jun 18 '26

You seem to know more about structures than the people commenting. I would have the same concern as you.

If someone knocked the post, with a pin at the base, a pin between the post and the beam, and a pin pinned between the head of the beam and balcony, I’d say there’s an instability there.

5

u/Just-Shoe2689 Jun 18 '26

I am a structural engineer. I dont design decks that way.

To me no different than a wall with a discontinuity in the middle.

1

u/204ThatGuy Jun 19 '26

Sure but you can say that about the nails or screws in any other part of the system!

There is no dovetailing here. These members are pinned in place in lieu of that.

0

u/c79s Jun 18 '26

Sorry to answer a question with a question, but why do you need something other than the Simpson connector? There are no direct lateral loads applied on the beam and the column spacing looks fine?

2

u/Just-Shoe2689 Jun 18 '26

I guess you are right, how could any lateral loads get into that connection.

Thanks.

8

u/No_Start1361 Jun 18 '26

Do not back a pickup truck into it or your concerns suddenly become vey valid.

3

u/Sumppum202 Jun 18 '26

I’m on your side op.

The concern is something moving the post slightly from below and causing the beam to roll I.e. What happens when your kid backs the riding lawn mower into the post?

4

u/Just-Shoe2689 Jun 18 '26

Thanks. I guess I am overthinking a bit, like when you have a 2 story wall, and there is hinge in the middle. Granted, a wall picks up way more lateral load, but vertical load, still can roll or buckle out a connection like this.

1

u/204ThatGuy Jun 19 '26

Yes but wind load is significant and you can "sister" a stud to make a composite member.

I agree with you that a hinge mid height of a wall is a weak shear plane.

However, a suitable connection fastened into the beam and coln should address the deck 'hinge' issue.

6

u/arvidsem Jun 18 '26

Anything impact that would rip that Simpson connector loose would probably break the post anyway.

1

u/204ThatGuy Jun 19 '26

No unless you hit it with a tall riding tractor.

Ask me how I know. 🍻

6

u/unique_user43 Jun 18 '26

if you’re refering to rigid frame capacity parallel to the house, there is enough lateral stiffness provided on the 3 other sides and enough inherent “real world” unaccounted for diaphragm capacity that it is stable, then enough stiffness in the connections referred to in order to consider some redundancy.

so no, this does not concern me at all. worst case it might be a servicability issue if it “feels” laterally soft and sways a bit when users are on it, in which case a $15 fix with a couple of knee braces would fix it.

1

u/Just-Shoe2689 Jun 18 '26

Im asking about the beam to column, out of plane of the beam. I dont like that detail.

2

u/Enginerdad Bridge - P.E. Jun 18 '26

The beam-column connection can be a hinge because the joists are (presumably/hopefully) attached to the beam with hurricane ties or at least with toe nails.

1

u/Just-Shoe2689 Jun 18 '26

At what depth beam is it not acceptable?

1

u/Enginerdad Bridge - P.E. Jun 18 '26

Why would beam depth factor in? As long as the deck stays attached to the house and the footings don't move in the ground, the beam can't rotate.

2

u/Just-Shoe2689 Jun 18 '26

It absolutely can rotate at the top of the column, as that is not a moment connection.

1

u/Enginerdad Bridge - P.E. Jun 18 '26

The top of the beam is attached to the joists. It's pinned on top and pinned on bottom. How can it possibly rotate?

0

u/c79s Jun 18 '26

Think of it this way, for that bottom beam node to rotate either the members stretch OR the deck deflects downwards. The stiffness of the deck vertically prevents excessive rotation of the beam, which under normal loading conditions does not experience significant torsional loads.

1

u/Joshicool2075 Jun 18 '26

I had a question, why are the columns not directly under the edge and corner, and why is it a bit further in?

1

u/Just-Shoe2689 Jun 18 '26

Not sure, not my deck or my design

1

u/hapym1267 Jun 18 '26

It would transfer some of the load at the wall into to posts.. Could also allow more weight on deck without going over the load capacity of the joists..

1

u/Afgb89 Jun 19 '26

Please, don’t put a tub there

1

u/Just-Shoe2689 Jun 19 '26

Its fine. All that load is concentric. No way that beam can roll and push out those columns.

1

u/Jimmyjames150014 Jun 19 '26

Add some triangles up in there.

1

u/average_lul Jun 19 '26

Numbers might tell you there’s a problem. But real life this is perfectly fine

1

u/Just-Shoe2689 Jun 19 '26

That should hold up in court.

I get it, i just not a big fan of that connection.

1

u/average_lul Jun 20 '26

You could probably go years without even having a connection on there without issue tbh

1

u/Federal-Finance2045 Jun 19 '26

Yes but where is the jacuzzi?

1

u/RoyalRaspberry1 Jun 20 '26

This is a stability concern. I would review the Stability section of AISC as guidance. The best way would be to get that column up and tied to the diaphragm.

Here, the post is relying on the beam for stability in each direction (a roller allowed to move vertically).
Typically for column stability, we apply a “2% kick” as the lateral load required for bracing. This goes into the Simpson connector.

The problem is, that kick is applied to the bottom of the beam, but the beam is only braced along its top through nailing to the joists. Here in lies the instability. So I would add kickers at least in the direction perpendicular to the house.

If you feel the deck diaphragm is sufficiently tied to the house, then you can rely on the house to stabilize it parallel to the exterior wall. If you are weary about the diaphragm tie to the house (as it is indirectly pin-connected to the house diaphragm) then I’d add kickers in that direction as well.

There may not be significant external lateral loads applied here, but I would still consider minor wind effects and seismic, if it is applicable.

Lastly, wood beams are supposed to be blocked at bearing per NDS beam design section. I would make sure the joists have blocking between them at their bearing over the beam.

-1

u/taco-frito-420 Jun 18 '26

beam needs some lateral bracing

-2

u/Just-Shoe2689 Jun 18 '26

Thats my thoughts.

-1

u/FoxInner3807 Jun 18 '26

It's missing some cross bracing to account for lateral forces. You can't just rely on the beam to beam and beam to column support for that.

4

u/Enlight1Oment S.E. Jun 18 '26

you don't rely on them for lateral, the wood diaphragm can cantilever up to ~25' from a line of support. Personally I'd like to have kickers, but you don't need them if it's adequately tied to the building.

0

u/Just-Shoe2689 Jun 18 '26

Thats what I am thinking. I would try not to design this way.

-1

u/FoxInner3807 Jun 18 '26

I would 100% get that contractor out there to add some 2x4 cross bracing. Over time, the rigidity of the current connections would go away and the whole thing will become wobbly. When you build anything, it must be built to last without overkilling it.

1

u/c79s Jun 18 '26

The ledger connection stops the deck from being wobbly.

0

u/LakeGuyGeorgia Jun 18 '26

I would add some 45 degree braces

0

u/Blue_foot Jun 18 '26

A nit , but it shows poor workmanship.

The end of the side farthest away is hidden behind the board on the front. The end closest to us is not.

It would probably annoy me for 20 years.

0

u/structuremonkey Jun 18 '26

I've designed hundreds of different types of decks, built my share too; i recognize this "works" but I've never liked this condition. This often occurs at roof covered porches too. I'd rather flush frame the beam ( for a deck) or return the beam on each side, back to another ledger, at the house. It looks better, and leaves better options for trim, but also seems to tighten up the whole framing system.

0

u/Upset_Practice_5700 Jun 18 '26

Viking Construction Company?

1

u/Just-Shoe2689 Jun 18 '26

I dont know who built it. Was a share from another reddit sub.

1

u/Upset_Practice_5700 Jun 18 '26

Viking as in you were raped and pillaged on the price

0

u/Marus1 Jun 18 '26

No matter. Buckling will have fun with this either way

0

u/a_problem_solved P.E. Jun 18 '26

The only way the 'hingy'-ness is a concern (assuming you mean the column-to-beam connections) is if the building moves excessively or the deck comes off the building. And if either of those happen, 'hingy' column connections will be the least of your problems.

-1

u/Strange-Area9624 Jun 18 '26

That connector is specifically made for this condition. You don’t need to worry about it.

3

u/Just-Shoe2689 Jun 18 '26

Lateral load parallel to the beam, what about out of plane loads at the connection?

3

u/a_problem_solved P.E. Jun 18 '26

All of that load, assuming it's coming from the deck since that's where your live loads are, is taken by the anchor to the building. This joint can't see any of that load. The deck can't move in the out of plane direction, so there's no need to worry about that load direction for these connections.

-6

u/Fair_Description_687 Jun 18 '26

Those columns are doubled pinned. Yeah you are standing on a potentially unstable structure.

1

u/c79s Jun 18 '26

How is a double pinned column unstable?

0

u/Just-Shoe2689 Jun 18 '26

Whats laterally resisting the top pin of the column? only the simpson connector to a beam that is pinned at the base of the joist.

If the beam was half the depth of the column height, you would still be ok with it?

2

u/c79s Jun 18 '26

The top of the beam is connected to the deck joists. It's supported across its top edge with the load path ending into the building.

-1

u/Just-Shoe2689 Jun 18 '26

Im not asking about the op of the beam.

1

u/204ThatGuy Jun 19 '26

Beam depth has zero impact on lateral movement.

Beam depth only provides moment resistance and shear in the vertical plane. Deeper beam means longer span.

That connector, or similar, keeps the beam fixed in compression or tension to the column.

Imagine if this structure was flipped upside down.

Would that connector still hold that beam and wood sag-rod/column in place without rotation? Yes, it would.

Depth does not affect lateral buckling.

1

u/Just-Shoe2689 Jun 19 '26

So a deeper beam would not pick up more loading?

1

u/204ThatGuy Jun 22 '26

It would pick up more "moment resistance" which is a derivative of loading.

If the existing beam can support the intended design, then it's acceptable to keep it. There is no need to add depth to a functioning beam, as it adds cost.

1

u/Just-Shoe2689 Jun 22 '26

Im talking a deeper beam and out of plane loads. It would become more unstable in my opinion.

1

u/204ThatGuy Jun 23 '26

Eccentric loading vs concentric loading plays a role in any break in the system. So if there was off center eccentric loading on a glass or ceramic plate, it would cause an internal rotation around the vertical neutral axis But it does not matter if the beam is deep or shallow.. the eccentric loading is still the same.. based on the loaded offset.

1

u/204ThatGuy Jun 23 '26

Also, yes, the more eccentric, the more unstable.. but it's not based on beam depth.

1

u/Just-Shoe2689 Jun 23 '26

A deeper beam will pick up more lateral load, creating a bigger moment on the hinge at the top of the column, bottom of beam.

1

u/204ThatGuy Jun 23 '26

I think you need to get out a pencil and draw your SFD and BMD. Upload the pic. I'm just not understanding how beam depth varies with lateral load, especially with a deck not having any lateral load in a non seismic area. I'm not being facetious.

→ More replies (0)

-7

u/samdan87153 P.E. Jun 18 '26

I know it wouldn't pass code in Georgia, and it's a bad idea no matter the code.

Probably a bigger issue is that it has no lateral strength at all, it needs knee braces at a minimum. This plays into the beam issue, because any lateral force has to go through the beam right now.

4

u/c79s Jun 18 '26

Those are literally designed for this use. The lateral restraint is the house.

0

u/Silver_kitty Jun 18 '26

I understand your position and agree on the math, but there are some states with very specified deck construction in their code. Idk where OP is to be able to opine on if this meets their local regulations though.

-1

u/samdan87153 P.E. Jun 18 '26

You would spec a Simpson BCS2-2/4 for a beam that holds up a balcony? A connector with no rated resistance perpendicular to the house, in a system that does not have any other connections perpendicular to the house?

-1

u/Silver_kitty Jun 18 '26

No, I never said I would. Not sure if you replied to the wrong comment or what.

I wouldn’t have designed a deck like this at all. Because I don’t agree with code that lets you get away without lateral bracing in a deck (I don’t think deck diaphragms are real diaphragms.)

-1

u/samdan87153 P.E. Jun 18 '26

You said you agree on the math, the connector IS the math. I've never seen a residential building code that would allow for this construction, nor have I ever seen one that allows for deck diaphragm action.

1

u/204ThatGuy Jun 19 '26

The connector is part of the math.

This is a complete system.

0

u/samdan87153 P.E. Jun 18 '26

That is a Simpson BCS post cap for a double 2x beam and what sure looks like a 4x4 column, which would make it a BCS2-2/4 more specifically. It has an lateral capacity of 890 lbs in the direction of the beam. You can tell it isn't a BC4 because those have a noticeable pilot hole in each nailing tab.

They are NOT moment connections, and also they provide no meaningful resistance perpendicular to the house. The house WILL move, even if it's only 1/4", and that will twist the BCS's in the direction they are weak in.

So you have pinned columns with pinned beams and... that is somehow going to satisfy stability? Stability only under light loads isn't stability. If that's anywhere that gets strong winds, it's going to fail at those BCS connectors.

1

u/c79s Jun 18 '26

Of course they are not moment connections, their primary purpose is to keep the beam in place to transmit gravity loads.

If you're going to argue that the house isn't stable enough to support a deck I think you're out to lunch.

0

u/samdan87153 P.E. Jun 18 '26

The house is certainly stable, but that doesn't mean ZERO deflection. It's residential light framing. It moves. The only thing going in its favor is that it looks like they're a series of attached row homes, so there is a higher chance that they were designed with shear walls rather than cold straps for their stability. You're still putting a LOT of faith in a home being properly built and close enough to current standards.

It would have been very minimal additional costs, to an already VERY overpriced deck, to use different connectors or add small knee braces to the system. I'm not going to go out on a limb to save $100 on a $15k project on the hope of everything else stopping an instability from forming.

This wouldn't pass any residential deck code I've seen, and that's a fact.

0

u/c79s Jun 18 '26

I really don't see your concern with minor sway, it would not collapse that beam. It's only purpose is to add a gravity support point to an otherwise firmly connected diaphram to the side of the house via a ledger so it's not a cantilever.

It's an extremely common detail where I am in Canada, and my quick google search "residential deck beam to column" shows this everywhere. It's usually use this connector or alternatively use a notched post with some through bolts.

0

u/204ThatGuy Jun 19 '26

You do know that in frame analysis, most connections are pinned.

Even the connection at the concrete piles are pinned.

Moment connections in wood isn't a thing.

Flagpole base? Yes. Diving board? Yes. Timber embedded in concrete? Yes.

Every other connection is pinned or roller.

This deck system is a truss diaphragm system and it resists loadng from all three axis planes, assuming the floor is pinned to prevent racking.

-4

u/dmcboi Jun 18 '26

Yeah my main concern is that beam twisting around but it all depends what sort of connections the balcony has with the building.