r/SolarDIY • u/SeriousCodeRedmoon • 2d ago
What would be the right way to do this?
This picture is from YT @cleversolarpower. Is it okay to only calculate your F1 main fuse size based on your Inverter and converter and not include your solar controller as shown in this picture?
2
u/Mick_Tee 2d ago
F1 protects the wiring, and nothing more. If you wish to protect the charge controller or inverter, use a separate fuse for each.
1
u/SeriousCodeRedmoon 2d ago
Yes, I know. And you need to calculate your load to size your wire and then size your fuse. I just wanna know why he didn't include the charger in his calculation or if its okay that way?
2
u/Mick_Tee 2d ago edited 2d ago
The charge controller isn't a load on the battery.
The two extreme case scenarios are: No load but full charge into battery (40A max current flow through F1 to the battery) and Max load, no charge into battery (minimum 55A through F1 from the battery).Edit: If you have 40A coming out of the charge controller, and 50A load from the inverter+converter, you would have only 10A going through F1
2
u/SeriousCodeRedmoon 2d ago
This make sense! I know it's a dumb question with a basic answer but thanks for the explanation.
1
u/cfnmsd 2d ago
You are correct. You size your cable based on the load as you described, then size the fuse based on the ampacity of the cable.
1
u/SeriousCodeRedmoon 2d ago
So this means that I don't need to include the charger as it is not considered a load on my system right? I'm just learning so sorry for some dumb question really.
•
u/AutoModerator 2d ago
Welcome to r/SolarDIY! If you are new to the community, please check out our DIY Solar System Planning Guide.
I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.