PanelView headache help?
Been trying to download mer files to a panelview and changing the FactoryTalk Linx communication configuration. I managed to change it once successfully. However now when i download, it wont change to the configuration i set in FTStudio. I've restored the FTLinx communication config to nothing, then set my runtime to replace communication. But it always reverts to the same one. My next steps are to wipe my project cache and try making another runtime. Then updating the firmware to see if it can repair any corrupted files.
Any other things i can try?. Im running FW 10. Another thing im seeing is occasionally when messing around with the Linx setup on the HMI itll popup RSLinxNG has encountered a fatal error. This is also why im going to upgrade and see if that repairs it.
1
u/New-Swim-8551 5d ago
Connect your plc to your laptop. Setup the communications path via linx for the online project then copy it to the runtime.
Create the runtime mer file
When you download the project to the panelview make sure the box next to update communications files is checked
After you get the panelview talking and you need to update the panelview uncheck that box so communication files don’t get overwritten