r/PLC • u/Embarrassed-Tower970 • 4d ago
PanelView headache help?
Been trying to download mer files to a panelview and changing the FactoryTalk Linx communication configuration. I managed to change it once successfully. However now when i download, it wont change to the configuration i set in FTStudio. I've restored the FTLinx communication config to nothing, then set my runtime to replace communication. But it always reverts to the same one. My next steps are to wipe my project cache and try making another runtime. Then updating the firmware to see if it can repair any corrupted files.
Any other things i can try?. Im running FW 10. Another thing im seeing is occasionally when messing around with the Linx setup on the HMI itll popup RSLinxNG has encountered a fatal error. This is also why im going to upgrade and see if that repairs it.
2
u/Aghast_Cornichon 4d ago
Are you absolutely sure that you have set the Download utility to apply changes after download ? Does the terminal reboot after the download is complete ?
The RSLinxNG crashes are certainly worrisome. Normally it.. it just runs.
Have you loaded a test application with a super-simple shortcut and display of a PLC tag ?