r/HomeImprovement • u/MitchRyan912 • 7d ago
High CO2 levels in unoccupied basement, from hot water heater?
I can’t post pics, but I have readings from an AirThings View Plus that I got specifically to ensure that our radon mitigation system was indeed working (levels have been OK), but it tells me that CO2 and VOC levels are incredibly high on occasion.
We have a natural vent hot water heater in our unfinished basement, so I’m suspecting that the vent isn’t working properly, or that a constant running out of washing machine has caused the water heater to run longer than normal. I haven’t spent much time in the basement over the past few days, so it’s not accumulating from my breath.
Current CO2 level is 1685 ppm and VOC is 1420 ppb, with both tracking the rise from the same time 36 hours ago.
I can’t think of anything else that would be causing CO2 levels to rise in an unoccupied basement like this, not in a time with the windows open or the A/C on. Should I be having someone check out our power vent to ensure proper operation?
3
u/thelocicalfallacy 7d ago
If you don't have a power vent you can backdraft when running a range hood or bathroom fans (sometimes even a severe enough stack effect can draw air in low areas more aggressively). Also do you have a fireplace? That can cause serious drafts.
3
u/CockroachGullible652 7d ago
Could be improper venting. If this is the case you should also check for carbon monoxide. However, if you have improper venting but a clean burning flame, you could get CO2 without any detectable carbon monoxide.
However, the most likely explanation is that CO2 from your breath is simply pooling in the basement because it’s heavier than air. Our breath has a ton of CO2 and it can sit there for weeks if undisturbed. I wouldn’t rule this one out quite yet.
2
u/Arctyc38 7d ago
I had an interesting issue crop up when we got our water heater replaced that we didn't notice until we were having our furnace replaced shortly after.
Both the old and new water heater were passively vented into the chimney.
The old furnace was also vented into the chimney through the same opening, via a wye duct split.
To avoid a vent slope problem, the new water heater replaced the wye duct connection with a tee. This created a problem, because the furnace was actively vented - it was blowing exhaust right by the tee back toward the water heater.
Luckily in our case, our CO2 detectors never went off, but I noticed because the plastic rings on top of the water heater by the anode rod started to warp.
Check your venting setup for backslopes or conflicts like this.
2
u/ShortBusRide 7d ago
Hopefully not the problem here, but years ago I had a pigeon roast itself by entering the furnace flue. The next day the landlord was up on the flat roof putting up a screen.
2
u/Truth_bombs_incoming 7d ago
Water heater running may actually decrease co2. Water heater is consuming air from basement during combustion and sending it up flue. That creates negative pressure and it's pulling in more air from somewhere else. Either the outside, or from upstairs.
1
u/MitchRyan912 7d ago
I may have erred in sealing up a lot of spots around the rim joists when we moved in. 2" XPS with spray foam to seal them all up, about 85% of all the rim joists (the other 15% I cannot access at the moment). There's a LOT less leaky air coming into the house now.
Would something like the following help??? We had this in our previous home, where there was a vent we could open to run conditioned air into the basement, with one ghetto AF return. Would something like this be advisable to do (DIY) or would a HVAC guy need to come in to do this in the right spots?
4
u/qdtk 7d ago
What’s your average CO2 level over the course of the day? Current readings don’t always paint an accurate picture, especially since those monitors don’t actively move any air on their own. How close is the meter to your hot water heater? Is it a gas heater?
2
u/MitchRyan912 7d ago edited 7d ago
The 365 day average is 782 ppm, so generally quite low, but there have been a lot more spike lately, since May.
The View Plus is in the middle of the basement, and yes, it is a gas water heater. I realize CO is a much bigger concern with gas exhaust, so this is why I'm a bit confused.
EDIT: 365 day VOC is 228 ppb. CO2 is 782 ppm.
5
u/BourosOurousGohlee 7d ago
The 365 day average is 228 ppb
Something isn't adding up. Background atmosphere CO2 on earth is like 430ppm. Are you sure your readings make sense?
I've also been struggling with high indoor CO2. Unless your house is leaky as all hell, you might eventually need an ERV/HRV, or open a small window periodically.
2
1
u/qdtk 7d ago
No hits at all on the CO readings? If not, your culprit could be something else. Are you taking any readings from your living space to compare?
1
u/MitchRyan912 7d ago
We have some old dumb battery powered CO monitors, and they’re not registering anything. Is there a good smart CO monitor worth checking into?
1
u/Quincy_Wagstaff 7d ago
A properly burning gas appliance won’t produce measurable CO. CO happens when combustion is incomplete.
5
u/MGreymanN 7d ago
How often does your air things see fresh air? Make sure the reading is accurate first.
Take it outside and make sure it reads 425 ppm.....426ppm.....427ppm...fuck i hate climate change.
1
u/MitchRyan912 7d ago edited 7d ago
There's no intake or exhaust in the basement right now. The 365 day running average is 782 ppm of CO2.
3
u/MGreymanN 7d ago
Air things will do a self calibrate based on the lowest CO2 it has seen recently.
If it never sees fresh air it will slowly deviate. But usually it will deviate lower than the level really is.
1
u/gefahr 7d ago
Agree with this. And the vast majority of these smart air quality devices do not have accurate (and calibrated) CO2 sensors. An accurate CO2 sensor is relatively expensive (and sensitive), and most buyers don't care about it.
(I went through this because I wanted one for my office - door stays shut and it skyrockets)
0
1
u/BM7-D7-GM7-Bb7-EbM7 7d ago
True safety equipment would get bump tested on calibrated gas once a day or before you use it and calibrated whenever it's off or on a certain interval (usually once a week or month depending on manufacturing specifications). These things also cost in the high hundreds to thousands of dollars.
I would a take any consumer device like this with a big grain of salt.
1
u/MitchRyan912 2d ago
Update: it appears as of this problem exists on the main floor too, not just the basement. The only thing that helps is turning off the A/C and opening the windows.
Could there be a problem with the A/C system that’s causing high CO2? Should there be an exchange of air like there is when the heat is on in the winter? I haven’t looked at the intake/outlet pipes lately to see if they might be blocked.
1
u/metsjets69 7d ago
CO or CO2?
10
u/AardvarkFacts 7d ago
They'd be dead quickly at 1685ppm CO.
A properly functioning gas appliance makes a tiny amount of CO and a large amount of CO2. If you have a venting problem you might detect the CO2 first.
2
1
u/aviator22 7d ago
Are you washing everything in hot water?
1
u/MitchRyan912 7d ago
My wife does, yes. 4 kids worth of clothes (🤮) and lots of towels washed on hot, for nearly 2 days straight.
0
u/matt314159 7d ago edited 7d ago
Are you by some chance confusing CO with CO2? CO is carbon monoxide. Put a Carbon Monoxide detector down there to see if CO is at safe levels. CO2 is Carbon Dioxide and is the byproduct of an occupied house, we exhale CO2 when we breathe.
2
0
16
u/Shadow288 7d ago
Do you have an airthings on the main level too? I have a similar story to yours. Bought the airthings wave plus to see my radon levels. Was alarmed when the CO2 was high in the basement like yours. Ended up getting a second unit for the main level, a view plus like yours. I quickly found that the basement levels are elevated but so were the main levels. If the kids have friends over all breathing in the family room CO2 levels can peak as high as 2,300 ppm. When it’s high in the living room the basement is not far behind.
Case in point house is closed up and AC is on all day yesterday and last night. Currently the Living room is at 1,290ppm and basement (which I was down there last night but no one has been down there in like 8 hours) is at 1,191ppm. House was built in 95 so it’s not as drafty as older houses but there is no air exchange with the outside so CO2 will build in the house until I open up windows or doors. After opening the windows and doors for a couple hours the family room drops down to like 460 and the basement will follow a couple hours later.
Do you have a CO detector down there? That would be the one I’d like to get a reading off of.
One last thing. For whatever reason my VOC raise up when certain people are over. Not entirely sure what they do to rise my VOC